I have an omron plc(cpma1) and I have one left input for two opto switch sensors for the operator to insert his/her fingure in each sensor to activate a press. I need the switchs to activiate only if they are within the time I set,if time expire for either switch,the input to plc does not turn ON. I tried to use two timers with not much success. Does any body thier know how to acheive this task without programming the plc?(no unsed inputs avialable or an expansion module). | |
| Top | |
| Table of contents |
RE: Timming issue,
Steve Bailey, Feb-11-01, (1)
RE: Timming issue,
Bob Earnheart, Feb-12-01, (2) RE: Timming issue,
iant, Feb-12-01, (3)
RE: Timming issue,
Steve Bailey, Feb-12-01, (4) RE: Timming issue,
iant, Feb-13-01, (5)
RE: Timming issue,
Chris@TECH3, Feb-13-01, (6) |
| Lobby | Topics | Previous Topic | Next Topic |
| Messages in this topic |
Steve Bailey
- (749 posts) ![]() |
Feb-11-01, 05:23 PM (EST) |
| 1. "RE: Timming issue" | |
Two-hand control is not a function that should be controlled by the PLC. You should use hardwired, standalone devices designed for the application. | |
| Top | |
Bob Earnheart
- (37 posts) ![]() |
Feb-12-01, 01:04 AM (EST) |
| 2. "RE: Timming issue" | |
I do agree, that you have some serious safety issue here but I will give you a suggestion. Take the two switches and have each control a dry contact relay. Put two NO contact (one from each relay) in series with a timer that will reset if either relay outputs are broken. This way your operator will always have to have both hands on the run switch before the machines main contactor latches in. Even if the PLC fails, your operator will still have one hand on one switch and one hand on the other. You are, don't forget, pointing a smoking gun at yourself and the operator by using a PLC in this way. Better thing about it. | |
| Top | |
iant ![]()
- (150 posts) ![]() |
Feb-12-01, 07:18 AM (EST) |
| 3. "RE: Timming issue" | |
just a side note . All safety aspects should be properly investiated before you attempt any PLC button control. | |
| Top | |
Steve Bailey
- (749 posts) ![]() |
Feb-12-01, 07:34 AM (EST) |
| 4. "RE: Timming issue" | |
The thread I was referring to is titled 'Press Brake Monitor' and was begun by Wayne on 1/14/01. The applicable OSHA standard is section 1910.217. Here's the link: | |
| Top | |
iant ![]()
- (150 posts) ![]() |
Feb-13-01, 07:20 AM (EST) |
| 5. "RE: Timming issue" | |
I could not remember Steve. | |
| Top | |
Chris@TECH3
- (2 posts) ![]() |
Feb-13-01, 12:56 PM (EST) |
| 6. "RE: Timming issue" | |
You need to purchase an ANTI-TIEDOWN safety relay which will have two palm button unputs & one or more outputs.The Timing & safety are already built in so all you have to do is hook it up. It will cost between $400-$500 but are OSHA approved & will save you the time | |